Re: Im running Lookout 6.2 and having trouble communicating with some GE Versamax Micro PLC's. Any driver issues I might need to know about?

Ryan,

 

In the alarm log it states "No communication response from GE Versamax".  I did do the diagnostics on the driver, the only thing I can see is a section that says "Open socket: Waiting for connection to complete, 0x2733".  You would think it would be a networking issue, but everything else on our network is working with no issues.

Active Participant
Ryan.S
Posts: 1,671
0 Kudos

Re: Im running Lookout 6.2 and having trouble communicating with some GE Versamax Micro PLC's. Any driver issues I might need to know about?

Can you create a new process with just one driver, and add a connection to that register? I want to know whether that register doesn't work at all or it just happens in your current application.

Ryan Shi
National Instruments