ni 9219 Analog input not working correctly

Hi,

 

I have connected Analog voltage of 5.2v to Ni 9219 CH1, Pin 4 & 6. but the reading i am getting on labview is 1.8v.

please find the attached screen shot.

 

Note: in the screenshot, block diagram, CH2, CH3, CH0 are not connected.

0 Kudos
Message 1 of 4
(2,800 Views)

You should attach your actual VI, a screenshot will not help others to help you.

By the way, you do not need to use your mobile phone to make a photo, any OS can do a screenshot 🙂

http://www.howtogeek.com/226280/how-to-take-screenshots-in-windows-10/

0 Kudos
Message 2 of 4
(2,764 Views)

hi , thanks for response.

i have attached the VI.

 

PC was not connected to network that time, so used mobile:P

0 Kudos
Message 3 of 4
(2,754 Views)

Hi Rudra,

 

attaching a FPGA VI without the project it is used in is senseless as all FPGA definitions/properties are missing…

 

I have connected Analog voltage of 5.2v to Ni 9219 CH1, Pin 4 & 6.

How did you configure your NI9219 module?

For measuring voltages you should use pin 4 & 5 - atleast that is what the manual says… (RTFM!)

Best regards,
GerdW