05-07-2014 04:25 AM
Hi,
When I connect to my cRIO-9073 an error message show up that it could not find all the libaries.
When I Ignore this and continue i am unable to load my VI's on the host PC and the real-time target.
I think I have installed all the necessary software on the cRIO.
A description of the problem can be found in the attached PDF.
The labview program can be found in attachement.
Best regards,
Jasper
Solved! Go to Solution.
05-12-2014 07:10 AM
Hello Jasper,
I have seen this issue before in combination with a (availible) memory problem on the controller. I can see you have quite a lot installed on the cRIO controller. The cRIO-9073 is around already for a couple of years and is limited in terms of avaiable memory comparing to our newer controllers. I saw you are using LabVIEW 2013 which has a bigger footprint then the LabVIEW versions that where around when the cRIO-9073 saw the daylight. I would advise to format the controller and only install the bare minimum which your application needs to the controller and try again. That way we can check whether this issue arrizes from a memory issue or something else.
Regards,
05-12-2014 12:10 PM
The memory use was indeed the problem. Now i have installed the minimum of software on the cRIO and the program runs fine.