SIT Initialization Simulation Error 54

Solved!
Go to solution

Hello all,

 

I have been going through the SIT examples, and have opened the "batch simulation.vi" example. Then, I have modified it so that it runs the sinewave.mdl from the sine wave example. This went all good and well. Then, I decided that I wanted to run the sinewave.dll on my PXI-8101. At this point, when I click run, it gives me the error:

Error 54 occurred at TCP Open Connection in NI_SIT_userAPI.lvlib: SIT Initialize Simulation.vi.

 

I think I might have missed a step somewhere, but I don't know. All I did was open the VI and click run.

 

 

Thanks.

Download All
0 Kudos
Message 1 of 3
(2,232 Views)

Never mind error 54. I am now getting error 56 TCP read error.

 

Exact same VI.

0 Kudos
Message 2 of 3
(2,223 Views)
Solution
Accepted by topic author Bladhart

Hello,

 

Is the PXI that you are deploying to a Real-Time PXI? It seems that you are getting this error because you are not specifying a driver VI for the model dll. You need to create and specify a driver VI when deploying to a RT target. Take a look at this link and it will help explain it in further detail.

 

David A.

National Instruments
Applications Engineer
Message 3 of 3
(2,212 Views)