05-23-2014 04:24 AM
Hi,
I didn't get an answer on the french forum. I try here.
I have a problem with the "MB Serial Slave Demon vi" (NI MODBUS). In fact, when I open a dialog box (file or message) in a loop parallel to "MB Serial Slave Demon.vi", the "MB Serial Slave Demon.vi"stop communication with the Master (read / write registers). The problem is that the ExecVI method (sorry i have french version) in "MB Serial Call Wait on Query.vi" (see picture below) does not give the hand until the dialog box is displayed. Why?:
Attached "MB Serial Example Slave.vi" example modified, i added in the event structure an Add button to see the problem. This example can be tested with "MB Serial Exemple Master.vi".
Any idea?
Thank you
Solved! Go to Solution.
05-25-2014 01:27 PM
I don't understand why the method does not give the hand. But, to solve the problem, I substituted "MB Serial Call Wait on Query.vi" by "MB Serial Wait on Query.vi".