02-03-2015 11:37 AM
Hi I am a biginner in cRIO. Playing with cRIO-9012, NI9421.There is an example program in Labview named " NI 94xx Input - Getting Started - Scan Mode". its a basic program just to show the LED status when there is something in DIO1. I implimented the program by changing the target chasis. To see how it works, I used a calibrator to send some voltages to NI9421. The LED is actually turned on at 8v. My question is how can I turned it on even in lower voltages like 2v, 3v, 5v. Somebody please help me out which settings I need to change.? I attach the screen shots of the program and the example file from labview.
Solved! Go to Solution.
02-03-2015 11:45 AM
02-03-2015 01:24 PM - edited 02-03-2015 01:29 PM
Thanks and sorry if I explained that wrong. The NI example that I am using is about Digital input. Any NI 94xx series can be used. I tried to input a counter/pulse but it doesnt read that. What I am looking for is to read a triggering pulse of any voltage level. Right now it is only reading when the voltage lavel is up to 8 v.
02-03-2015 01:32 PM
If you look at the data sheet for the 9421, it is a 24V logic digital input module. It states that an off state is 5V or less and an on state is 11-30V. Anything in between should be considered unstable.
You can't just pick the logic level for the input module.
02-03-2015 01:59 PM
Some how I thought that its 0-10v. I should have read the data sheet before using that.Thank you very much.