How Fast are cRIO Inputs Updated?
Thank you Crossrulz. I have created the following two VIs, with the top one running on the cRIO and the bottom one running on my host PC, is that correct?
Message 11 of 15
(1,361 Views)
I got the network stream transmitting some data, but the data still only seems to be changing about every 1 second. Am I supposed to get the data off the cRIO by some method besides the shared variables?
Message 12 of 15
(1,354 Views)
Accepted by topic author Gregory
Gregory,
Speed Issue:
1) Check cRIO Scan Period (right-click cRIO in project) set to at most 100ms
2) NI-9208 Conversion Time - right-click module - High Resolution 52ms - High Speed = 2ms
    Note these are PER channel times - 10 channels = 20ms
PC Communication - Network Streams definitely the way to go.
At least on your cRIO (both is better) you should detect a connection error and retry.
Otherwise you would have to restart the cRIO when restarting the Host application.
steve
Help the forum when you get help. Click the "Solution?" icon on the reply that answers your
question. Give "Kudos" to replies that help.
Message 13 of 15
(1,351 Views)
Thank you stevem!
It is a 16-channel module, so what I thought was a 1 second delay was actually an 832ms delay (16 channels * 52ms). After changing the module from high resolution mode to high speed mode I can read much more quickly!
Thank you also to Crossrulz and Corey, the suggestions about network streams will be useful as I continue to work more with cRIOs.
Message 14 of 15
(1,347 Views)
My pleasure. Glad you got it resolved! Didn't even think about the module's configuration. Good thinking stevem.
Corey Rotunno
Message 15 of 15
(1,325 Views)
