06-24-2015 09:05 AM
So Google search suggest that Baud Rate in VISA Read and Write needs to be changed to match the settings in NI MAX. Am I heading in the right direction ? How would you suggest me to do that ?
Felix
06-24-2015 09:19 AM
06-24-2015 10:25 AM
06-24-2015 11:21 AM
This is the Driver that I got from NI. http://sine.ni.com/apps/utf8/niid_web_display.download_page?p_id_guid=0150785855373A2DE0440003BA7CCD...
It says Serial Interface and I am using Serial Connection on the Communication Board. I am not sure what I am missing. Could you clarify ?
06-24-2015 12:43 PM
06-24-2015 01:41 PM
Thank you for your reply. The *IDN? command was sent to the Tidal Engineering Synergy488 Board which has serial and GPIB connection on it. That was where I succeeded in communicating in NI MAX. The Watlow manual only contains ModBus Commands. The Synergy488 Board manual does not contain any SCPI command or serial command that I can use to program. I am little confused.
06-24-2015 02:38 PM
06-24-2015 02:41 PM - edited 06-24-2015 02:41 PM
When we bought the Chamber. We specify that we want GPIB and Serial Communication. The Watlow F4 communicates using ModBUS. So the manufacturer put a Synergy488 board there to enable serial and GPIB communication with PC. So the Watlow connects with the Synergy 488 Board and the Synergy board connects with PC
06-24-2015 04:00 PM
I was able to write and read register using a simple serial VI. You are right that Watlow Driver was not written for my application.
Thank you so much for your help.
Felix