Watlow Ez zone Modbus control with Labview

Hello !

 

I'm trying to control an Ez Zone Watlow temperature controller through modbus via Labview. I've downloaded the basic VIs provided by Watlow to do this, and had them converted from v 8.6 to 8.0 (I'm running on Labview 8.2). The Ez Zone is connected to the computer (Win XP SP3) with a serial RS485 crossed cable on the PC's serial port COM1.

 

When I run read.vi (attached below) in Labview, and try to read a random parameter, it returns a empty string and this error :

 

 

Error 1 occurred at an unidentified location

Possible reason(s):

LabVIEW: An input parameter is invalid. For example if the input is a path, the path might contain a character not allowed by the OS such as ? or @.
=========================
NI-488: Command requires GPIB Controller to be Controller-In-Charge.

 


I don't really understand how this VI works, because althought it calls a .dll file, I don't see how the connection to the instrument is made.

 

The serial port is configured as follows :

 

Bits/s : 9600

 

Data = 8 bits

 

Parity : none

 

Stop : 1

 

Flow control : none

 

... which is the default communication configuration on the instrument.

 

 

Thanks for your help,

 

Paul

0 Kudos
Message 1 of 3
(4,135 Views)

Hi

 

The only problem I remember having with this controller was that the RS485 connection is half duplex NOT full duplex. I only used this to set the IP address using their supplied software as the controller had a Ethernet\ModBus adaptor and I used that for all the LabVIEW programming.

 

John

 

ps Are you running the initialize VI first?

0 Kudos
Message 2 of 3
(4,117 Views)

I am having the same problem. Did you ever fix this?

 