Cannot connect to DeviceNet. Getting Error -2147036511

I'm getting the following error when connecting to DeviceNet 15.0 from LabVIEW 2015 SP1 through the PXI-8532 DeviceNet interface connected on a  PXI-1042Q chassis:

 

Error -2147136511 occurred at Open DeviceNet Interface.vi 

Possible reason(s): 

An internal fault occurs in the NI-DeviceNet driver. Please contact National Instruments and provide the information from the file %InstallPath%\National Instruments\NI-Industrial Communications for DeviceNet\niDnetErr.log.

 

The Code is as simple as I can get it: 'Open DeviceNet Interface.vi' and 'Close Object.vi' from the Industrial Communications subVIs.

 

The niDnetErr.log has the following information:

Severity: Error

Type: System Service

Component: 27

File: 1

Line: 88

Code(hex): 0x00000420

Info(hex): 0xec01c058

 

0 Kudos
Message 1 of 2
(3,595 Views)

Solved the problem by moving the PXI-8532 from slot 8 to slot 2 on the PXI chassis and getting all other cards in the system out..  I'm successfully communicating to a Brooks SLA5850 mass flow controller.