NI Home
Cart Cart | Help
You are here:
Reply
Member
AGovi
Identifying channels on cFP AO 200
I have a cFP 1808 controller that I am configuring for a heat exchanger application. All the input and outputs are 4-20 mA current signals. I have added cFP AI 200 for receiving current signals from the heat exchanger unit and cFP AO 200 for sending current signals to the i/p (current to pneumatic) converter devices. I have 3 outputs, so I need to use 3 channels out of the available 8 channels of output in the AO 200. However, I am not able to understand, what constitutes channel 0 or 1 or 2 for that matter. Is the channel number decided by how I wire the outputs to the AO 200, i.e does each terminal 1-32 on the connector block have a channel assigned to it?
In other words, if I want to send out a signal to i/p device 1, using FP write in LabVIEW, what channel should I use? How do I decide if it is one channel or the other?
Thanks in advance.
Active Participant
Wayne.C
Re: Identifying channels on cFP AO 200
Each channel of cFP-AO-200 has 4 terminals associated with it.  The channel you use is determined by the terminals you connect to.  See table 1 here.
Member
AGovi
Thanks Wayne. I intend to send out a 4-20 mA range current signal through the AO 200. So if I were to select channel 1 and use terminals 4 and 19 would that work? Do the terminals have to be different if the output were voltage instead of current?
Active Participant
Wayne.C
First, carefully read the paragraph directly following Table 1.  Then take a close look at Figures 4 & 5.