I have 10 device on a FFB HI network, 7 of them can be link masters. Should I put all 7 as link masters to backup the primary LAS?
Solved! Go to Solution.
08-17-2011 08:03 PM
Hi,
There is no limit for the primary LAS backup number.
And in default, the link master device with the smallest address is the primary LAS.
So please modify your device address according to this rule.