Analog value read with DSC Module Modbus

Solved!
Go to solution

Hi, I have a Delta PLC with an AD converter module. I am using all four analog channels and in one of them I have a thermocouple that displays the temperature data on a microprocessor thermocouple meter. Nevertheless I want to display the data on Labview. The plc communicates with labview through the DSC Module from labview succesfully but I'm not able to read the data. Looking forward to your help.

0 Kudos
Message 1 of 2
(3,579 Views)
Solution
Accepted by topic author CarlosT

Found the solution; the addressing for the modbus master was different for this plc model so I looked for the Modbus address list for delta plc and the analog read was successful on labview.

0 Kudos
Message 2 of 2