Module Failure - Different Computer

I currently have a set up with the FP-1601, (2) FP-TC-120, and a FP-AIO-610 modules.  We are upgrading to a new computer so I copied the vi and the iak files from the current computer.  For some reason when the vi is run on the new computer I get readings from everything except the FP-AIO-610.  The program runs just as it should on the older computer.  The operating systems are the same and I'm using LV version 6.1.  Any suggestions?....Thanks.
LabVIEW 2016 - Windows 7

CLAD
0 Kudos
Message 1 of 3
(3,128 Views)
The probable cause is that the version of FieldPoint you are using was released prior to the FP-AIO-610 having been released. The simple solution is to go into MAX, select the IP address of your FP-1601 and choose Find Devices. By querying the devices, the FieldPoint software will identify the FP-AIO-610 as a module that it does not have a datasheet installed for, and will download the datasheet from the module.
 
Regards,
Aaron
0 Kudos
Message 2 of 3
(3,126 Views)
That did it!!...Once again this web-site pulls me out of a jam....Thanks Aaron.